DMC 1700 problem registering board in win,XP

Hello John,

It looks like your issue here is that you are mixing up the IRQ setting with the Address setting. The address, which can be configured from 512 to 1024, is not the IRQ setting. There are separate IRQ jumpers for setting the IRQ address.

The address you are referencing here is the "input/output" range, which is explained in the DMC-1700 user manual on page 20.
http://www.galilmc.com/download/manual/man_18x0.pdf

You should see on the bottom of the DMC-1700 there are a row of headers labeled IRQ5 through IRQ 15. Jumper one of those headers to set the IRQ in that range.

Sincerely,

Michael Cox
Applications Engineer
Galil Motion Control

Hello John,

It looks like your issue here is that you are mixing up the IRQ setting with the Address setting. The address, which can be configured from 512 to 1024, is not the IRQ setting. There are separate IRQ jumpers for setting the IRQ address.

The address you are referencing here is the "input/output" range, which is explained in the DMC-1700 user manual on page 20.
http://www.galilmc.com/download/manual/man_18x0.pdf

You should see on the bottom of the DMC-1700 there are a row of headers labeled IRQ5 through IRQ 15. Jumper one of those headers to set the IRQ in that range.

Sincerely,

Michael Cox
Applications Engineer
Galil Motion Control