HI,
Actually I am using Galil RIO 47142 PLC. The connection is establish but I dont know that how to read Analog values from the PLC. I have to read PT100 RTD Sensor value through PLC. Can any one help me....

Thanx
Mohit,.

Comments 1

troym_galil on 12/21/2015 - 08:42

Hello, Do you have Modbus TCP on your PLC? If so you can connect to the RIO and send Modbus commands to read the analog inputs. The RIO will also accept ASCII based commands over a TCP or UDP connection. You could send the command "MG @AN[1]" and the controller would respond with a ":" and the analog voltage at input 1.